Replacing analogue roomstat with Honeywell CM907; wiring?

CM907. Am I doing this right? I don't think I am. I don't have any other wires. Thanks ...

310320121181.jpg
 
Sponsored Links
CM907. Am I doing this right? I don't think I am. I don't have any other wires.
Are you replacing an old mechanical thermostat which had only two wires connected? If so, you are correct. The brown goes to A and the Blue to B. The blue wire should really have some red sleeving or insulating tape round it to show that it is the switched live.
 
Thanks Alex. This was helpful.
The Honeywell instruction were fairly clear but not on what to do with the old neutral.
 
Sponsored Links
PS it's worth knowing if the display fails they will replace the part F.O.C.
 