Currently I think what Sunray is saying is that with a single socket outlet the max you could load that socket to would be 13Amps.
If you plug an extension cable in with 4 outlets the maximum that single socket can provide is 13 Amps as fused by the plug on the extension cable.
What you're doing by adding an additional socket or 2 sockets in the case of going from a pair of singles to a pair of doubles is theoretically increasing the maximum load on that feed to 52 Amps. However that's where the design of the installation of the property comes into play.
The cable will be designed for a maximum current carrying capacity, and the associated fuse/breaker shall be appropriate to protect the cable from excessive currents which may result in excessive heat/combustion.
So although you theoretically could put 13 Amp loads into every outlet, your Consumer unit will protect the cabling infrastructure well below the 52 Amps. What your maximum allowable load will be is determined by you cable dimensions, this is then reduced for margin by your fuse/breaker.
Nothing you are doing is altering the characteristics of your installation, these limits will still apply.
If you were to take out a fuse/breaker and replace it with a higher current one because you thought it was necessary to allow full utilisation of the additional outlets then quite a few of us would have said................................... NO! Don't do that