I think that would be wise.There are other factors at play here too. At the moment I’m leaning more towards wanting to get someone to come in and do the work for me.
I think that would be wise.There are other factors at play here too. At the moment I’m leaning more towards wanting to get someone to come in and do the work for me.
OR a radial or a spur - either wrongly installed or installed with suitable cable.If you have 'two sets' of cable at the existing socket, 2x reds(or browns), 2x blacks (or blues), plue two earths, that simply means the socket is on a ring.
...but is indistinguishable from the other options.Nothing complicated about it, the ring begins at the consumer unit, goes round/through all the sockets, then back to the consumer unit.
If you have 'two sets' of cable at the existing socket, 2x reds(or browns), 2x blacks (or blues), plue two earths, that simply means the socket is on a ring. Nothing complicated about it, the ring begins at the consumer unit, goes round/through all the sockets, then back to the consumer unit.
Because we have too many things to plug in and not enough sockets and I’m not a fan of overloading extension cables!!Why go to all that trouble and expense, in my study, I just use a four socket extension lead with surge protection.
Hi Sam,Alright everyone, I’ve been doing a bit of investigation this afternoon and there doesn’t seem to be any rhyme or reason to how my sockets are wired. In the CU I have 7 MCBs controlling sockets. Six of those are 16A MCBs and seem to control no more than one or two sockets, and the 7th is a 32A MCB and seems to control everything else. Since I can’t guarantee whether these are ring or radial I’m going to just leave it in the hands of a professional.
Oh dear. The blind leading the blind
On a radial circuit all sockets except the last one, and any spurs of the radial have one cable. This means all the others have 2 cables
Alright everyone, I’ve been doing a bit of investigation this afternoon and there doesn’t seem to be any rhyme or reason to how my sockets are wired. In the CU I have 7 MCBs controlling sockets. Six of those are 16A MCBs and seem to control no more than one or two sockets, and the 7th is a 32A MCB and seems to control everything else. Since I can’t guarantee whether these are ring or radial I’m going to just leave it in the hands of a professional.
You either have a 2.5mm T&E Final Ring or a 4mm T&E Radial.
Hi Harry,Don't be put off by that Murdoc troll, simply find out which MCB supplies the socket we are interested in, and report back..
There are none so blind, as those who will not see, and you seem especially blind and irrelevant - posting unnecessary complications, despite many in here disagreeing with your stance.
Yeah that’s pretty much the paragraph that was concerning me!If it's this paragraph that's causing you concern.
'With the circuit isolated you can safely undo the screws on the front of the socket. If there’s just one wire per connector (earth, live and neutral) it means that the socket has already been spurred off another; you can change this into a double socket but you can’t spur off it to supply a new outlet. Two wires going into each connector indicates that the socket is either part of the ring main or that it is one of two sockets fed by the same spur. If you plan to swap a single socket for a double or add a new spur, you must make sure that the outlet is part of the ring main. To check, you need to run the continuity test in the next step.'
Then I would discount most of the stuff after you can safely undo the screws on the front of the socket. The Author is entirely ignoring the Radial type installation and assuming that every house only has Ring Finals installed so anything that's a single conductor must be a spur.
He's wrong.
Thanks for this. How would I determine the sizes of the cables?Hi Sam,
That's sound investigation.
What you've discovered (large assumption here on correct installation) is
You have 6 Radial circuits running to sockets (the 16Amp circuits with a single 2.5mm T&E connections)
You either have a 2.5mm T&E Final Ring or a 4mm T&E Radial.
I'm not sure I'm allowed to suggest what I would do next, but it would be around isolating your incoming supply and trying to ascertain the cable dimensions at entry into each breaker.
As someone has suggested if your cables are too short you can use inline Wago connector to extend the cable, ensuring it's the same dimensions as the installed cable.
If the 2 sockets you want to convert to 4 are on one of these radial branches then they remain appropriately protected by the 16 Amp Breaker.
If the 2 sockets you want to convert to 4 are on the arrangement from the 32 Amp breaker then with correct cable selection you will remain protected.
You are perfectly capable of doing this, you've already done work that allows you to know which outlets are connected to which breaker.