yeah it should but be sure to test and use safe isolation procedures, remember that the supply tails will ALWAYS be live!
The terminals on these RCDs are a tunnel tyoe it is my guess the terminal has been tightened up but with the busbar not in the terminal but behind it.
Thanks to all those who responded, I think it's all resolved now. (fingers crossed.)
I replaced the RCD, had to clean up the busbar but all looks good now.
Still wondering if people think this has been unsafe for the last 4 years?
I can't be sure, but the incomer looks like it's a 100mA one. Or it might be my eyes and a laptop size screen letting me down.
If it is 100mA I'll bet it's a time delayed one, and yes, such an arrangement was perfectly normal for TT installations, except this one has been badly split - all the sockets should be on the 30mA RCD.