Hi
Hope you guys can help me please.
I recently removed an old system gas boiler for a customer which was open vented and feeding a copper cylinder and heating circuit with no zoning. Its a 3 storey home which had storage heating in the top 2 storeys.
Sometime in the past another plumber ran two pipes ( flow and return) from the downstairs heating circuit to upstairs so radiators could be plumbed in upstairs at a later stage.
I removed copper cylinder, fitted a pressurised Ariston combi gas boiler to give the customer instant hot water. Used the old 22mm expansion and cold feed pipe to act as the return for the upstairs radiators and removed the expansion tank in the attic. I then used one of the pipes which the last plumber had ran upstairs to act as a flow for upstairs and fitted 5 new rads upstairs. I fitted 2, two port motorised valves on the returns to zone upstairs separately from downstairs.
Thought everything was fine until the following day the home owner rang to say downstairs was heating even when it was turned off. It's a small circuit with just 5 rads. 2 or 3 are heating pretty well, even though return pipe is closed off with the motorised valve, and stone cold.
Is this a one pipe circulation?
To fix it do I:
A. Fit another ABV
B. Motorised valve on the flow
C. Non return valve on the flow
E. ?
How do I prevent this happening in the future?
Any feedback much appreciated.
Thanks
D
Hope you guys can help me please.
I recently removed an old system gas boiler for a customer which was open vented and feeding a copper cylinder and heating circuit with no zoning. Its a 3 storey home which had storage heating in the top 2 storeys.
Sometime in the past another plumber ran two pipes ( flow and return) from the downstairs heating circuit to upstairs so radiators could be plumbed in upstairs at a later stage.
I removed copper cylinder, fitted a pressurised Ariston combi gas boiler to give the customer instant hot water. Used the old 22mm expansion and cold feed pipe to act as the return for the upstairs radiators and removed the expansion tank in the attic. I then used one of the pipes which the last plumber had ran upstairs to act as a flow for upstairs and fitted 5 new rads upstairs. I fitted 2, two port motorised valves on the returns to zone upstairs separately from downstairs.
Thought everything was fine until the following day the home owner rang to say downstairs was heating even when it was turned off. It's a small circuit with just 5 rads. 2 or 3 are heating pretty well, even though return pipe is closed off with the motorised valve, and stone cold.
Is this a one pipe circulation?
To fix it do I:
A. Fit another ABV
B. Motorised valve on the flow
C. Non return valve on the flow
E. ?
How do I prevent this happening in the future?
Any feedback much appreciated.
Thanks
D