I was originally going to do the outhouse in 6mm cable but 2 people have told me to just use 2.5 and they are electricians. i thought 4mm would probably be enough but 6 would be better. im thinking 32A maybe better and if needs be put in a 40A at a later date.
ban-all-sheds said:Who is going to be doing the work?
As explained before, the point of a separate circuit is not to deal with loading problems, it is to get the F/F off of an RCD protected socket circuit.YCWB said:im not sure on running in a seperate feed for the freezer? is this common place? i know the kitchen as a whole can be on a seperate ring but as only the living room and dining room will be on the same ring i didnt see this as much of a problem.
IMO you should be designing for radials, not rings, but people have different views.the upstairs ring will be on a seperate one. would it be better to have 3 rings, one upstairs, one downstairs and one for the kitchen? or would it be better design to use one ring for the kitchen and one for the rest of the house? i know this isnt set in stone and im sure a few people on here will have different views.
1) Do not have the outhouse supply cable on the RCD side of the house CU - put an RCD CU in the outhouse and run sockets & lights from that.Still not decided on best way to do the outhouse, probably leaning towards running 6m SWA straight from the CU right into the outhouse and then just a few sockets off that and one light. the RCD in the house will protect the downstairs ring and the outhouse. it could also do the upstairs ring but as none of the sockets are likely to be used for equipment outside then there is no special need.
SamySnake said:I was originally going to do the outhouse in 6mm cable but 2 people have told me to just use 2.5 and they are electricians. i thought 4mm would probably be enough but 6 would be better. im thinking 32A maybe better and if needs be put in a 40A at a later date.
The mcb is selected for the sole purpose of protecting the cable. Select the cable by calculating your design current, then look in your OSG and select a suitable mcb to protect that cable.
Unless he is registered with a self-certification scheme, and lies on official documents about him having done the work, this is not an option in its own right - it's part of the option of DIY-ing with advance notification to LABC.YCWB said:I know a guy who will do as somebody suggested, he will come and inspect the work on 3 visits and do the testing at the end.
Legally you must, if you DIY or if the work is done by a non-registered electrician.I can inform building controll and go through it that way
Yes - you have to pay them. This is not one of the things they are not supposed to do. When you submit a Building Notice you have to pay their fee - it's what the law says.but building controll in my area dont like anybody at all doing this and they are insisting on paying BC
You're absolutely right - they are not supposed to do that, and the belief of the ODPM is that it is unlawful for them to do that.and also paying an external contractor to come and test the work because they dont have electricians working for them. I know this isnt what they are suposed to do but that what they are insisting.
If you are genuinely qualified to the level that would allow you to register to self-certify, and the test equipment is in calibration, and you know how to use it, then why not register? You say that you want to do rewires in houses - i.e. you're going to encounter this notification issue again and again. Even if the LABC play ball and don't make you pay any more it doesn't take many notification fees to cover the cost of registering, and that's before you factor in the opportunity costs of dealing with the hassle, and the usefulness of being on friendly terms with LABC if you're into property development...I have an EAL domestic installer qualification which allows me to register with NIC, ELECSA etc. Im not an electrician by trade and dont need to get work as one so im not going to go with the NIC. I do need to be able to do my own rewires in houses but i dont make a living from it. I am in the property game.
I have access to a Megger MF 1502 and i have the Minor works, Electrical Installation and Periodic Forms. I also have all the approved docs (Part P, A, B, E, etc), onsite guide......
An interesting combination.....The outhouse will contain a washing machine.
There isnt a water supply
Fine - make sure your EFLI is OK on the outhouse circuit, as Ze can be high-ish with TN-S, and away you go.The house has a TN-S supply.
Really should be on the RCD5. Not RCD Protected - Electic shower - not decided on KW so will use 10 sqmm cable.
I assume you've done the volt-drop etc calcs, and that the cable will be deep enough, bearing in mind that concrete might be removed with powered tools & machinery in the future. Warning tape would be a good idea. And even though it's a small shed, someone might build a bigger one - the materials cost of 10mm² SWA is not much more than 6mm²...6. Outhouse - 32A mcb - Not RCD protected in house, but RCD in outhouse. 6 sqmm 3 core SWA. This will have a washing machine, tumble dryer, electric heater and one light. A trench will be dug, sand laid down, SWA ontop of the sand, sand ontop of the SWA and then concrete over the top.
Yup. If it were me I'd also seriously consider installing a cooker circuit just in case it's ever needed.After reading these posts i understand that it might be a better idea to have the fridge on a seperate radial that isnt rcd protected, and maybe a good idea to give the kitchen its own redail/ring circuit.
And problems with unbalanced loading, and problems with people spurring from it...I understand why BAS likes radials, they are less dangerous as a ring is subject to a break in the ring. If a break occurs the ring will still work but 2.5 cable isnt designed to carry 32A.
BAS said:Unless he is registered with a self-certification scheme, and lies on official documents about him having done the work, this is not an option in its own right - it's part of the option of DIY-ing with advance notification to LABC.
ban-all-sheds said:If you are genuinely qualified to the level that would allow you to register to self-certify, and the test equipment is in calibration, and you know how to use it, then why not register? You say that you want to do rewires in houses - i.e. you're going to encounter this notification issue again and again. Even if the LABC play ball and don't make you pay any more it doesn't take many notification fees to cover the cost of registering, and that's before you factor in the opportunity costs of dealing with the hassle
If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Are you a trade or supplier? You can create your listing free at DIYnot Local