Rewiring for a 10.8kW shower

I never said it was 35A.
To the op don't be misled by this bloke, your cable is rated at a maximum 35Amps and is not suitable for a shower larged than 7kw or 40A fuse/mcb.
I meant this one.
Because of the installation method, the 6mm cable will have a maximum rating of about 35A, so you are stuck with the 30A fuse.
Good grief. I think I've tired of trying to follow your wriggling around.

You might like to comment on why you changed your advice regarding thg maximum acceptable fuse for a cable with a mnaximum CCC of 35A from 40A to 30A between those two statements ... but I suggest that you don't hold your breathing while waiting for me to do any more wriggle-following.

Kind Reegards, John
 