I also think that you didI think i said that.If you have a 16a mcb fitted fine. If 32a you need to add the "return leg" to make a ring. And RCD protection and testing…and….. signed off by an electrician.
Kind Regards, John
I also think that you didI think i said that.If you have a 16a mcb fitted fine. If 32a you need to add the "return leg" to make a ring. And RCD protection and testing…and….. signed off by an electrician.
But we have no knowledge of the installation.If you have a 16a mcb fitted fine. If 32a you need to add the "return leg" to make a ring. And RCD protection and testing…and….. signed off by an electrician.
I believe that the technical term is "open-minded". (although I'm inclined to go along with your implied doubts!).I think you're being kind.
the cable is the normal socket cable running from consumer unit with fuse b32.
Yes its just a long spur.....
Get the stupid, ignorant, dangerous fool who did that, which was illegal and has put your life at risk, back, and demand that he puts it right. You should not have to put right the mess that the cretin left behind for you.the cable is the normal socket cable running from consumer unit with fuse b32.
As it is new the installer could have quite sensibly fitted a 4mm² 32A radial circuit.
the cable is the normal socket cable
Your implied point may, of course, well be correct - but I doubt that I'm the only one who has ever mistaken 4mm² T+E for "normal socket cable".As it is new the installer could have quite sensibly fitted a 4mm² 32A radial circuit.the cable is the normal socket cable
Krazaq - what news?What does the schedule on your Electrical Installation Certificate say about cable size, MCB rating, circuit type etc?