Hello!
Just after a bit of advice with circuit design if possible.
The circuit(s) are for our lounge and dining-room/office (odd combination I know!) in a terrace house and I'm wondering whether I should go for a ring main for the lot or have two radials, one for each room.
If I do the whole lot as a ring the total length of the circuit would be 50 m (including 10%) and would connect fifteen 2 gang 13 A sockets (I'm trying to eliminate extension leads!).
I calculated a worst case scenario for the load (everything was turned on at once, including hoover and three 100 W table lamps) then the current would come to 15 A. Is this how you're supposed do these calculations? I ask because this would limit the circuit length to 35.5 m on 2.5 mm² 2&E and I understand that the on-site guide puts the maximum length for 2.5 mm² 2&E at around 80 m on a 32 A MCB?
I'm also having problems calculating the earth fault loop impedance for this circuit. I have my part P certificate for the shower we had installed and this states the external earth fault loop impedance as 165 Ω. I've been following the tlc guide to these calculations and the examples they use have Ze of around 1 or less. Putting a Ze of 165 Ω into these equations would put the maximum circuit conductor length less than 0. I assume I've made an error here...!?
I was wondering if it would better to go for two separate radial circuits. This has some advantages as I can complete one circuit, get it tested and then move on to the next one. I've seen a comment about ring circuits having complications with respect to electromagnetic interference. While the floorboards are up I was thinking of getting some data cabling in and was wondering whether interference is something that should seriously influence the choice of circuit.
Last question if I may, if I go for radials then how fiddly is getting 4 mm² cable into 13 A sockets?!
Thanks in advance
Just after a bit of advice with circuit design if possible.
The circuit(s) are for our lounge and dining-room/office (odd combination I know!) in a terrace house and I'm wondering whether I should go for a ring main for the lot or have two radials, one for each room.
If I do the whole lot as a ring the total length of the circuit would be 50 m (including 10%) and would connect fifteen 2 gang 13 A sockets (I'm trying to eliminate extension leads!).
I calculated a worst case scenario for the load (everything was turned on at once, including hoover and three 100 W table lamps) then the current would come to 15 A. Is this how you're supposed do these calculations? I ask because this would limit the circuit length to 35.5 m on 2.5 mm² 2&E and I understand that the on-site guide puts the maximum length for 2.5 mm² 2&E at around 80 m on a 32 A MCB?
I'm also having problems calculating the earth fault loop impedance for this circuit. I have my part P certificate for the shower we had installed and this states the external earth fault loop impedance as 165 Ω. I've been following the tlc guide to these calculations and the examples they use have Ze of around 1 or less. Putting a Ze of 165 Ω into these equations would put the maximum circuit conductor length less than 0. I assume I've made an error here...!?
I was wondering if it would better to go for two separate radial circuits. This has some advantages as I can complete one circuit, get it tested and then move on to the next one. I've seen a comment about ring circuits having complications with respect to electromagnetic interference. While the floorboards are up I was thinking of getting some data cabling in and was wondering whether interference is something that should seriously influence the choice of circuit.
Last question if I may, if I go for radials then how fiddly is getting 4 mm² cable into 13 A sockets?!
Thanks in advance