Good day, folks,
I have an S-Plan system with a Baxi Solo boiler and Smiths Centroller 3000 programmer with room and hot tank senstats.
The system seems to be working OK, except that the boiler doesn't switch on when the room temperature drops below the Centroller setting until there is a temperature difference of about 3 to 4 degrees. I'm measuring room temperature close to the senstat and using several different thermometers.
In order to achieve 19-20 degrees in living rooms, the Centroller is set to 23 degrees. The Senstat has been replaced, with little change, and the clock settings work OK.
The programmed settings on the Centroller are retained correctly.
The circuit diagram on the Centroller installation instructions shows the Senstats connected to a "temperature control module", which has a physical connection to the clock, and presumably compares the Senstats with the programmed settings.
Or is there a problem external to the boiler/controller, such as a zone control valve malfunction?
I would very much appreciate advice from a competent person on the likely cause of the problem, as a replacement Centroller would be quite expensive.
With thanks - commelect.
I have an S-Plan system with a Baxi Solo boiler and Smiths Centroller 3000 programmer with room and hot tank senstats.
The system seems to be working OK, except that the boiler doesn't switch on when the room temperature drops below the Centroller setting until there is a temperature difference of about 3 to 4 degrees. I'm measuring room temperature close to the senstat and using several different thermometers.
In order to achieve 19-20 degrees in living rooms, the Centroller is set to 23 degrees. The Senstat has been replaced, with little change, and the clock settings work OK.
The programmed settings on the Centroller are retained correctly.
The circuit diagram on the Centroller installation instructions shows the Senstats connected to a "temperature control module", which has a physical connection to the clock, and presumably compares the Senstats with the programmed settings.
Or is there a problem external to the boiler/controller, such as a zone control valve malfunction?
I would very much appreciate advice from a competent person on the likely cause of the problem, as a replacement Centroller would be quite expensive.
With thanks - commelect.