"Where... "(not you can) I would think this means when you have had to rely on RCD for reasons above.Yes, but as we've discussed before, 411 actually appears to allow that 'primary' automatic disconnection of L-E faults can be provided by an RCD (the footnote to Table 41.1 says "Where compliance with this regulation is provided by an RCD ...."). Hence, it would appear that an RCD can provide both 'primary' and 'additional' fault protection - or am I misinterpreting?
Not CAN be used - only if unavoidable.As above, the regs seem to imply (actually, say) that an RCD can be used as a 'usual method' of satisfying 411.3.2.2 for primary L-E fault protection.
Perhaps 'faulty' wasn't the right word to use but if MCB disconnection conditions cannot be met (in 'normal' property) there must be a fault or faults.No argument there. I would personally actually say that that it was always bad practice to use an RCD 'because the installation was faulty', even if were a mansion!
Perhaps there should be a note under each regulation, and under each note, stating what was actually meant.
Perhaps this is why they are not statutory.