Removed from OSG in AMD 1??
I hadn't caught up with that update yet...
I hadn't caught up with that update yet...
I haven't seen the new OSG yet but, in Amendment 1, the statements in ('Informative') Appendix 15 about floor area change from, say:Removed from OSG in AMD 1?? I hadn't caught up with that update yet...
(which I reckon is weak enough, partcularly given the "has been")As a rule of thumb the floor area served has been limited to 50m²
So, as I said, no longer even a 'rule of thumb', and now essentially just a statement of historical fact. If I were in the game, I'd certainly see no reason to regard failure to 'comply' with that statement about history as being a 'deviation from BS7671' - what do you think?Historically the floor area served has been limited to 50m²
My guess could well be that the guy didn't really understand the principles of ring finals and put 16s in because 16 is half of 32.Probably just had 16A's to hand would be my guess.
That seems pretty likely. I'm also a little surprised how often one hears these stories about a ring final being converted to two radials as a lazy (or 'temporary') solution when a fault arises in the cable - why is it that such circuits seem so often to develop cable faults roughly in the centre of the ring?!My guess could well be that the guy didn't really understand the principles of ring finals and put 16s in because 16 is half of 32.
My guess could well be that the guy didn't really understand the principles of ring finals and put 16s in because 16 is half of 32.
Okay, what do you propose the design current to be then?
i would like to see a 4mm radial protected via a 32A mcb ideally for the appliances in this particular property. 2.5mm 20A would be ideal for the living room as it has a low load demand. but as a ring had already been installed i would prefer to reinstate the ring and do away with the radials.
This was done in the corrigendum to the BRB back in 2008.in Amendment 1, the statements in ('Informative') Appendix 15 about floor area changed
So it was - I'd forgotten that So, it hasn't been a 'rule of thumb' since 2008. No need for the pritt stick,though - the BGB has saved me from the need to do that!This was done in the corrigendum to the BRB back in 2008. Time to get a pair of scissors and a pritt stick out.
i know that this is safe but i am unimpressed with the possible load on the kitchen radial (2.5mm 16A 60898) as 2 appliances could overload the circuit.
Strange, now your saying that tripping has occurred due to overload.
Also, strange that the customer will call you out to replace a faulty socket but will happily live with having to reset the protective device from time to time. (Some people are strange).
So you are obviously aware of the faulty cable. Have you tested the cable and established the fault?
Why don't you clamp an ammeter in circuit and run some appliances and see what sort of load the circuit requires?
You might be interested to look at the article entitled "Amendement No. 1 2002 to BS7671 and ring currents" in the Spring 2002 edition of Wiring Matters. Despite the rather uninspiring title, this article includes a very interesting analysis of the loading on a kitchen ring when a washing machine, dishwasher and tumble dryer are started on their cycles simultaneously and an electric kettle used twice during the period the other machines are running. It concludes that this loading is (just about!) OK for most of the time with a 32A ring - but a 16A or 20A radial would clearly not be adequate for that loading.it can be tricky calculating the max demand on this circuit with out knowing the exact loading on each of the "utilization points". maybe you could steer me in the right direction and show how you would calculate design current for the kitchen radial taking into account it has four high loading appliances (washer, dryer, kettle and fridge) and 3 double sockets. my own calcs using diversity would place above 16A how about you.