You can fit them before the pump so it's on the negative side which may limit pressure jumps on initial startup but TBH it's just about limiting the flow to one direction.
It's a closed loop so the pump differential pressure is the same whether the NRV is before or after. In theory it's better after the pump, as that gives higher suction pressure (no NRV pressure drop) but in your case there is plenty of pump suction pressure either way.
It's a closed loop so the pump differential pressure is the same whether the NRV is before or after. In theory it's better after the pump, as that gives higher suction pressure (no NRV pressure drop) but in your case there is plenty of pump suction pressure either way.
Not just sealed systems, open vented systems as well.
Edit - I suppose you could say in this setup it's a closed loop when there's no HW drawoff. When there is drawoff it's a bit of both. But it doesn't make any difference, why do you ask?