shaver plugs in bathroom

Joined
3 Nov 2004
Messages
37
Reaction score
0
Location
Northamptonshire
Country
United Kingdom
I have installed a IPX4 fan with humidistat at the top of zone one near the ceiling with a pull switch by the door and a 30ma RCD outside the bathroom. Do I need a 2 pole switch as well or will the buttons on the RCD be enough to isolate it.
Also I want to put a 2 pin socket in zone 3, can someone tell me the requirement for that. I understand if I wire that from the trip as well it could cause problems.
 
Sponsored Links
Mars said:
I have installed a IPX4 fan with humidistat at the top of zone one near the ceiling with a pull switch by the door and a 30ma RCD outside the bathroom. Do I need a 2 pole switch as well or will the buttons on the RCD be enough to isolate it.
As your RCD is a two-pole isolator anyway, this should be fine. It allows you to properly isolate for maintenance.

Also I want to put a 2 pin socket in zone 3, can someone tell me the requirement for that. I understand if I wire that from the trip as well it could cause problems.
No sockets allowed in a bathroom, except electrically separated shaver sockets and SELV sockets.
 
Yes thats what I want to install a shaver/toothbrush socket in zone 3. Do I need to wire that through an RCD or can it come straight from the light ring.
 
Sorry, I didn't read the post title! (See my name!)

There's no need for an RCD and the lighting circuit is the usual source of supply.

(In fact, as there is electrical separation and no earth on the secondary side an RCD wouldn't operate anyway.)
 