He isn't. FCU ?Why are you suggesting running a unprotected spur ?
Not sure where you saw that quote, but it's not from the Wiring Regulations - they don't contain any prescriptive heights.Just seen a quote from the 17th edition "PVC insulated cable supported on catenary wire- height above pathway:3.5m min.
height above driveway: 5.8m min.
span: unlimited. "
I have given the OP three FCU options - all comply with the regulations.I thought the OP understood the FCU is at the house end ?
Why are you suggesting running a unprotected spur ?
DS
OSG. (Table 4B in my ancient {red} version) - so, as you say, not regulations.Not sure where you saw that quote, but it's not from the Wiring Regulations - they don't contain any prescriptive heights.
Even the OSG's 3.5m would be inadequate for many ladders, if carried vertically - mine is well over 4m.You must make sure that the cable won't be damaged by any reasonably foreseeable event. I guess at only 2.6m that includes carrying ladders, garden tools etc.
Not only does it nowhere say the OP cannot, 433.2.2. says he can.where does it say that the OP cannot JB the Ring Final circuit in the loft - run a rubber sheathed 2.5mm2 to the shed into the FCU and then onto his socket and or switch?
Whilst I would personally also want to see an FCU at the house end, it's very probable that a 32A MCB would afford adequate fault protection for the cable, and it doesn't really matter which end of the cable the overload protection is provided. However, only an electrician (or someone else 'in the know') could confirm that.I would still want to see the (13A) fused protection for the overhead wire at the house end ... if you do not do this, any fault on your bit of 1.5mm or 2.5mm cable is protected by the 32A mob in the consumer unit. - you know what can happen to overhead cables……
Use a Switched FCU in the shed as your light switch.Ok so a 30amp junction box in loft, rubber sheathed 2.5mm cable out to under eaves down wall to this( http://www.screwfix.com/p/bg-13a-switched-weatherproof-rcd-fcu/20523) mounted at about 2.5m from ground. 2.5mm rubber sheathed cable back up wall to as high as possible then across to shed supported by catenary wire. Cable in to shed to a double switched socket. Feed taken from that to a 5amp FCU thence to light switch and then light fitting. How does that sound? Sorry to have started a bit of flaming. Thank you everyone for your feedback.
Indeed (and a 3A fuse will be sufficient, no need for 5A). However, lest the OP misunderstands what you're saying, he will still also need a 13A FCU in the feed to the shed (at one end or the other, preferably the house end).Use a Switched FCU in the shed as your light switch.