So I am at my grandparents in Maidstone installing a Wireless Pyronix alarm in their bungalow.
To run power to the panel, I take a 1mm² T&E from a junction box in the loft (what is on one of the lighting circuits) to the FCU and then to the Pyronix panel.
First check for power at the panel and then do a 3 wire no-trip Zs test; So far so good.
I then move on to do an 500V IR test between L and E; turn off the circuits MCB and all lights/devices on that circuit and end up getting a very low readings around 0.05MΩ! I then get no power when I go to re-power the panel up.
Turns out the junction box in the loft what I thought was a permanent feed of the lighting circuit, was in fact the switched output that goes to all the external lights around the outside of the bungalow.
The switch that feeds that JB and thus the outside lights was On when I was doing my inital tests and Off following my IR test.
Yes you read it right, I had wired the alarm up to the switched output of the outside lights.
Lucky I have found another lighting junction box that I correctly traced back right by the one that I taped into under the fibreglass insulation that needs redoing as all the CPC's are twisted together outside the JB with no sleeving.
Regards: Elliott.
To run power to the panel, I take a 1mm² T&E from a junction box in the loft (what is on one of the lighting circuits) to the FCU and then to the Pyronix panel.
First check for power at the panel and then do a 3 wire no-trip Zs test; So far so good.
I then move on to do an 500V IR test between L and E; turn off the circuits MCB and all lights/devices on that circuit and end up getting a very low readings around 0.05MΩ! I then get no power when I go to re-power the panel up.
Turns out the junction box in the loft what I thought was a permanent feed of the lighting circuit, was in fact the switched output that goes to all the external lights around the outside of the bungalow.
The switch that feeds that JB and thus the outside lights was On when I was doing my inital tests and Off following my IR test.
Yes you read it right, I had wired the alarm up to the switched output of the outside lights.
Lucky I have found another lighting junction box that I correctly traced back right by the one that I taped into under the fibreglass insulation that needs redoing as all the CPC's are twisted together outside the JB with no sleeving.
Regards: Elliott.