a 10A breaker on the same line as a 13A fuse will break first. This is rather fundamental stuff
If we are talking fundementals, something in my "basic principles" folder says that it is fundamentally bad practice to have a lower current CPD upstream of a larger one!
Taylortwocities, there are exceptions, and this is one. The point is not to remove a heavy appliance from a unit and superior overall protection of the cable, flex and appliance by sizing the DP MCB/RCBO to suit, not just slapping in a 16A MCB/RCBO because that is what most do. If an appliance only draws say 8A then a 10A MCB/RCBO will be fitted raising the overall protection.
stillp, MCBs is what I mean, sorry.
Igiffer, double pole micro breakers are available. They are more common in Germany and France. Also DP RCBOs are available. A Consumer Unit with DP RCBO's on all circuits is the ultimate protection. The best. One I may aim for. Check out the DP jobs. I am not going to Google for you, but type in 'DP RCBO' and lots comes up. The cheapest is £13 and then upwards. They are there, not in
Screwfix, but there.
ABB make a DP MCB that are available in a
"single module" width, the same width as a normal single-pole MCB. If space is a problem then these are ideal. I think they are quite expensive, so if space is not a problem then these are the way to go.
ban-all-sheds, the cost of DP RCBOs on a handful of circuits for a flat is not a great cost but the superior protection is worth the cost. Also DP RCBOs divides and rules. Only that circuit trips in the case of a fault not the whole place and the neutral is also switched out. It is also easier to test. I intend to have these DP MCBs or preferably DP RCBOs/DP MCBs also as isolators in the Consumer Unit for heavy appliances, so saving costs elsewhere and eliminating those ugly FSUs on walls. Put it all in the Consumer Unit all at one point.