That doesn't need a 45A supply...andrew55 said:we have a summer house at the bottom of the garden. and like a small plunge pool - with a 5kw heater. Don’t get excited its nothing special just a Argos pool that’s be built under the decking - previous owners.
How did you resolve that?What worries me is the guy that owned the house before was a right cowboy! As when we first moved in that was connected so it bypassed the meter.
4mm² is rated at 37A if it's just clipped to the surface of a wall, but introduce any thermal insulation, or bunching with other cables, into the mix and the capacity drops off, quite conceivably to well under 30A.andrew55 said:So where do I stand, as this cable is right on the limit with 30amps? (although it seems to have managed up until now).
Also bear in mind that all cable ratings assume that the temperature of the copper core will rise to 70°C, which is pretty hot - well over the pain threshold if you should touch it, so it only needs a bit of extra heat from a poor connection, and hey presto - damaged insulation.
It is more likely to be threaded through holes in the noggins?Suppose I should swap it for thicker cable but how much work will be involved in this? My house is a 15year old Barrett style one so has an outer single block wall and then plasterboard walls sorta an inch or two off this wall (if that makes sense) - would the cable be fixed to the wall as it runs up into the attic making swapping it with thicker cable a really big job?
However it is installed, it won't be that easy to replace, I imagine, so if you're going to do it, you might as well put 10mm² in, then you have the option of a more powerful shower when the current one packs up...