John is right, there is more to the issue than the PC power supply tripping it out, 16A isn't enough for a whole house (the french restrict to either 6 or 8 sockets on each breaker)
A B32 will have similar magnetic tripping properties to a C16
Just for some background info, MCBs trip by two mechanisms, a thermal overload one, for example connecting 25A of load to a 16A breaker, this is exactly the same in a B16, C16, and D16, the second one is a magnetic part thats used for short circuits and earth faults that are low impedance and cause many amps to flow B is somewhere between 3 and 5 times the rating, C between 5 and 10 and D 10 and 20.
The reason that you can't just swap them without testing, is you have to make sure that if a fault occurs (eg. live wire touches case) the fault to earth won't be less current than you need to operate the magnetic part of the device. Electricians have the equipment to measure EFLI (earth fault loop impedance)
Whole house on 16A is not good regardless of whether its B or C curve, however if it was just a circuit serving one socket by the PC, then a C curve breaker could be the answer (pending ELFI checks)
A B32 will have similar magnetic tripping properties to a C16
Just for some background info, MCBs trip by two mechanisms, a thermal overload one, for example connecting 25A of load to a 16A breaker, this is exactly the same in a B16, C16, and D16, the second one is a magnetic part thats used for short circuits and earth faults that are low impedance and cause many amps to flow B is somewhere between 3 and 5 times the rating, C between 5 and 10 and D 10 and 20.
The reason that you can't just swap them without testing, is you have to make sure that if a fault occurs (eg. live wire touches case) the fault to earth won't be less current than you need to operate the magnetic part of the device. Electricians have the equipment to measure EFLI (earth fault loop impedance)
Whole house on 16A is not good regardless of whether its B or C curve, however if it was just a circuit serving one socket by the PC, then a C curve breaker could be the answer (pending ELFI checks)