No, don't know if the kick parameters can be set in the Vaillant controller. a 10C dT.on should be OK especially with evacuated tubes, if that doesn't cure the problem maybe consider changing dT.off to 6C. or maybe just extending the swimming pool circ pump to 1900hrs instead. Sensor trends would really tell a lot but all mine only display the preceding hour with 1min updates.
Cylinder priority
Two solar-charged cylinders can be connected to the
heating installation. You can use the PRIO cylinder priority
function to define which cylinder should be
charged as the highest priority.
This is normally the drinking water cylinder. The cylinders
can only be clearly identified via the cylinder sensors
(cylinder 1 = Sp 2; cylinder 2 = SP 3).
You can only change this setting at the installer level.
The cylinder that has been assigned the highest priority
will always be charged if the collector temperature is
greater than the sum of the actual temperature in the
cylinder and the activation difference specified. The
heating of the cylinder will stop once the maximum temperature
for the cylinder is reached, or if the collector
temperature is less than the actual cylinder temperature
plus the set deactivation difference.
The second cylinder can only be heated when the first
cylinder is not being heated. The charging of the second
cylinder is interrupted for at least 5 minutes every
15 minutes to check whether the cylinder can be
charged with the highest priority. The same activation
and deactivation conditions apply here as well.
Cylinder priority
Two solar-charged cylinders can be connected to the
heating installation. You can use the PRIO cylinder priority
function to define which cylinder should be
charged as the highest priority.
This is normally the drinking water cylinder. The cylinders
can only be clearly identified via the cylinder sensors
(cylinder 1 = Sp 2; cylinder 2 = SP 3).
You can only change this setting at the installer level.
The cylinder that has been assigned the highest priority
will always be charged if the collector temperature is
greater than the sum of the actual temperature in the
cylinder and the activation difference specified. The
heating of the cylinder will stop once the maximum temperature
for the cylinder is reached, or if the collector
temperature is less than the actual cylinder temperature
plus the set deactivation difference.
The second cylinder can only be heated when the first
cylinder is not being heated. The charging of the second
cylinder is interrupted for at least 5 minutes every
15 minutes to check whether the cylinder can be
charged with the highest priority. The same activation
and deactivation conditions apply here as well.
Last edited: