Wattage is never quoted.Whats the maximum wattage and amperage a 1.5mm2 cable can handle?
Amperage is determined by the type of protection (eg cartridge or rewirable fuse or circuit breaker), the conductor material (there are materials other than copper), insulation material (standard PVC is rated up to 70˚C, other materials can go higher), installation method (a cable buried in insulation will heat up more, and thus carry less current safely, than one buried in plaster), and grouping (if you put several cables together then you have to derate them).
But for example, a 1.5mm² thermoplastic, non-armoured, copper cable, 2 core, single phase AC, ambient 30˚C, conductor 70˚C, is stated as 20A for reference method C (clipped direct or directly buried in masonry) or 17.5A for reference method B (enclosed in conduit or trunking). The volt drop is 29 mV/A/m. Even after applying a correction factor for the type of fuse (which doesn't seem to be given for "13A" fuses), that's plenty of headroom for something running at around 7.5A max.
The cable capacity tables in BS7671 (aka "the regs") run to nearly 50 pages !
The voltage capacity of the cable is determined by the type and thickness of the insulation.
Wattage is then the product of multiplying rated current by operating voltage - though you may also have to factor in power factor if it's significantly different from 1.
CorrectIf a 1.5mm cable is rated at 14A, then technically it's way higher than the 13A fuse that would be inside the plug anyway, so the fuse will blow before the wire has any issues.
Yes it will, it's got only 60% of the copper and thus will have higher resistance, thus more power created by the current flowing through that resistance. But, it's well within the rating of the cable and generally you can ignore the difference.But does a 1.5mm cable rated at 14A get any hotter drawing 13A than a 2.5mm cable drawing 13A?