I think the following should do it:
get MKs largest CU enclosure (the one that takes 21 modules total)
get two split load kits.
get appropriate MCBs/RCDs
The split load kit contains cables designed to tap off the busbar and neutral bar for the non-rcd side to feed the RCD side, I can't see any impediment to using two of them to feed two seperate RCD sides.
I was thinking along those lines, though I would need to find a good way to add another neutral bar for the second RCD.
I did email Hager as they have a dual RCCB board with a single switch disconnector and got this reply.
Hager tech support said:The VC810C has an isolator switch controlling both an
80amp100mamp rcd and an 80amp30mamp with 10 outgoing
ways which can be configured in any way from 9 +1 to 5 + 5.
......The isolator switch only switches the 2 RCD's and not
any individual mcb's.
........The VC866H is a 100amp isolator switch controlling
2 x 80amp30mamp RCD's with 6 outgoing ways on both RCD's.
This consumer unit will comply with the 17th edition regulations as
they stand at present.We will be bringing out other units within the
next month or two that will also comply .
Aside from the argument about whether a consumer unit can 'comply' with the 17th regulations if installed in the incorrect way or situation, it seems to me that the suppliers are missing out on a marketing opportunity here. Or is what I have read elsewhere true in that some of the additional RCD requirements were only included at a late stage and they are still catching up?
I may well end up with a twin RCD board, protected by a Time Delay RCD in a separate enclosure. But given the number of quite large and/or oddly shaped houses around my area with TT supplies that are never going to be PME'd, I will keep looking for a 'neater' solution.
Gavin