Need a little help please. I fitted a new honeywell 4073 3 port valve on saturday and was unable to get the boiler to fire afterwards for HW and CH. ive checked my wiring a million times and finally sussed there is no boiler and pump live feed to the airing cupboard. im at a loss as to why?
i had a look at the wiring for the controller(st699b)
if i remove the fascia and connect the link wire from L-5-8 and switch it to L-4-8 i can get HW controlled nicely by the slider and stat but no CH
confused!
Y-plan system
look at the wiring for three port valve; you are missing a wire me thinks
I think now it will be a million plus 1
What can I say that I have not already said in my post. LOOK AT THE Y PLAN wiring.
Why would you want to move the wires link from L-5-8? :rolleyes:
because if i connect the link wire to L-4-8 i can at least get some hot water. L-5-8 does not supply a feed to my airing cupboard at all, so i have nothing
I dont understand what you mean by a missing wire and my system is wired the same as a y plan diagram.
your ST699 is faulty,for starters but why have you got a cable connected to number 4 anyway? That's not yplan,
well it is but not one that is wired as per your valve if what you are doing is making a difference
I take it there is one connected already prior to moving the link?
what make was the previous valve?
Matt
Matt
Thanks Matt, the ST699 is not faulty. i thought it was too so i bought a new one and it made no difference!
In trying to diagnose the fault i looked at several wiring diagrams for the st699, one of which counted from right to left not left to right, leading me to think the link wire should be on terminal 4 not terminal 5, i hope you see what i mean? the wiring diagram is the "honeywell 4073a" .pdf
when i wired the link wire incorrectly like this i discovered i could have hot water! (we have had no hw or ch for 4 days! getting a little desperate here)
i have also discovered if i add an additional link wire from L-4 4-5 5-8 i can also have CH but not both simultaneously.
the previous valve was a SUNVIC SDM 1901
The motorised valve actautor wiring need not be connected, and you should still have hot water during HW calling. So, your wiring is incorrect!! :cool:
even with the MVA wiring disconnected the boiler would still need a live feed to fire up.
If you have wired as per: http://www.honeywelluk.com/Documents/Full-Install/pdf/1083.pdf, then with the link on the ST699 as shown L-5-8, you will get live fed to your tank stat on C or 2 (depending on HW on or HW off). So not sure what you mean by ‘L-5-8 does not supply a feed to my airing cupboard at all’.
What wiring diagram have you used?
That link you posted doesnt work but thanks, i'll see if i can google it
i used a honeywell .pdf but this one is identical http://octaveblue.co.uk/c_heating/hw1_ch1.htm
ah, that link works without the comma on the end, yes thats the one im using
what i meant by" L-5-8 does not supply a feed to my airing cupboard at all" is, if i put my circuit tester on the orange wire from the 3 port valve in the connector block in my airing cupboard, there was no voltage
im off work today so am trying different things. I have re-wired the ST699 back with the link wire in the correct position. would a faulty HW thermostat cause this issue? what i mean is... if the HW thermostat was stuck in a constant satisfied state, would this prevent the boiler from firing even the CH?
Sorry about the comma!
I think it’s unlikely that your tank thermostat is faulty, but possible. To check, try disconnecting it and testing continuity through it. If possible, change its state by varying the set temp.
With HW on at the programmer, you should get live at terminal 6 of the wiring centre. If the tank stat is demanding heat you should get live at terminal 8. That is the feed to the boiler and pump which should then run. This is as shown in the octaveblue animation.
Thank you.Ive just tested that and the thermostat (L641a) works correctly, but, when the stat reaches the desired temp, shouldnt terminal 7 then become live? HW off? i have this connected to the grey wire on the 3 port valve but this wire is not live at any point