Never used a beam with a plate less than 10mm.
will speak with structural tomorrow beam is UB254x102x22 with an 8mm welded bottom plate looks like the plate that is rotating only a beam has no flex really dont want too add a mid point post if i can help it. just measure ed of beam and looks like builders have installed correct beam.
It will always flex to some degree but if designed to its serviceability limit state the deflection should be acceptable, designing to its ultimate limit state will hopefully prevent beam failure.You don't need to prop beams, as they do not rely on the masonry immediately above it like common steel lintels do.
A steel beam is designed to limit state, ie to support its design load without flexing.
Correct.The blockwork is crap though. No bricklayer laid those.
The beam should be propped.
Blocks should be half bonded.
Wouldn't surprise me if there was meant to be brickwork 'arching' above that beam externally.
Crap builders.
Ask for a copy of his calcs and post them up. As for the 20mm its all a question of aesthetics, Deflection in a beam should generally be restricted to 1/360 but as the beam seems to be ok at its current loading it looks like its down to the deflection of the plate and whether 20mm is considered visually acceptable to the end user i.e. you.will speak with structural tomorrow beam is UB254x102x22 with an 8mm welded bottom plate looks like the plate that is rotating only a beam has no flex really dont want too add a mid point post if i can help it. just measure ed of beam and looks like builders have installed correct beam.
A plate should not deflect when just part loaded with one course and a part course of blocks!the beam seems to be ok at its current loading it looks like its down to the deflection of the plate and whether 20mm is considered visually acceptable to the end user i.e. you.
Well assuming the load on the plate is acting 0.125m away from the edge of the beam and the load on the plates is 100kg/ metre run then I calculate the deflection as 0.007mm. based on deflection = W.L.L.L/3EI but I could be wrongA plate should not deflect when just part loaded with one course and a part course of blocks!
It should (will) have maximum deflection when the maximum load is applied, so in this case it will only get worse.
Not withstanding the buckling note, thats interesting as I did a quick check using the Blue Book and depending what roof span and loads were taken there seemed to be a possibility that it could suffice. As a matter of interest what loading did you take for the span.Never ever use a 254x102 UB as a lintel above a doorway. They are useless unless restrained as they are too slender and will buckle long before they reach their full bending resistance.
A 254x102 simply isn't sufficient for the span (my quick check indicates a 254x146x43 as an absolute minimum), but the other issue is torsion (which will mean a 254x146x43 won't work either). The load of the outer leaf on the plate will put torsion into the beam that 254x102s simply can't handle. I guarantee that check hasn't been carried out.
It's a flat roof. Vertical loads.Would buckling not be restricted by the roof joists to some extent?
Yes the joists would tie into the beam and stop sideways/ buckling movement?It's a flat roof. Vertical loads.
No, three reasons (off the top of my head).Yes the joists would tie into the beam and stop sideways/ buckling movement?