Hi, my first time here.
3 years ago after buying my flat I replaced an old Tricity 3.4KW storage heater with a new Sunhouse Automatic 3.4KW. I also have an old Tricity 2.4KW storage heater.
Sunhouse was connected using a 2.5mm heat resistant cable via what I later found out was a 13A led switch which gradually died (well fried really) as it was getting hot and was replaced with a 20amp switch which seemed to get warm rather than hot. The 2.4KW tricity has never had switch heating problems but I also changed its 13A to 20A.
Both heaters are separately connected into a dedicated 63A 2 Module Double Pole RCD consumer unit made by CED with each heater having its own 32A-SP MCB.
Right from the start if the input dial on the Sunhouse was set to 5 or over (1-6) the main RCD would trip. So I kept it to under 5 and all was well. Recently I noticed that the 20A switch on the Sunhouse is also getting very hot and consequently tripping the RCD at input settings even less than 5.
I am now thinking of putting a 32A switch on the sunhouse as from my school physics the heating switch means resistance and assume a 32A switch may resolve the problem.
Finally both heaters are connected to the consumer unit using external cables not embedded within the walls which must have been done by the previous owners. And that the flat used to have the old wire fuses which I had replaced with 2 consumer units, one for the heaters and one for the rest of the flat.
Does this problem ring a bell for anyone?
3 years ago after buying my flat I replaced an old Tricity 3.4KW storage heater with a new Sunhouse Automatic 3.4KW. I also have an old Tricity 2.4KW storage heater.
Sunhouse was connected using a 2.5mm heat resistant cable via what I later found out was a 13A led switch which gradually died (well fried really) as it was getting hot and was replaced with a 20amp switch which seemed to get warm rather than hot. The 2.4KW tricity has never had switch heating problems but I also changed its 13A to 20A.
Both heaters are separately connected into a dedicated 63A 2 Module Double Pole RCD consumer unit made by CED with each heater having its own 32A-SP MCB.
Right from the start if the input dial on the Sunhouse was set to 5 or over (1-6) the main RCD would trip. So I kept it to under 5 and all was well. Recently I noticed that the 20A switch on the Sunhouse is also getting very hot and consequently tripping the RCD at input settings even less than 5.
I am now thinking of putting a 32A switch on the sunhouse as from my school physics the heating switch means resistance and assume a 32A switch may resolve the problem.
Finally both heaters are connected to the consumer unit using external cables not embedded within the walls which must have been done by the previous owners. And that the flat used to have the old wire fuses which I had replaced with 2 consumer units, one for the heaters and one for the rest of the flat.
Does this problem ring a bell for anyone?