Spotted this on a job today. Guess it's been there a while.
Both fuses are live. I only tested with a voltstick as I didn't want to disturb the cutout, so not sure if they're on the same phase.
The feeder cable is a 3 wire PILC, and the cores look about 25mm², so it doesn't appear to be an old 3 phase and neutral supply.
This is in a domestic property in a suburban street not too far out of the city centre.
I was there pricing up for rewiring the place. Currently there appears to be no earth from the suppliers, no bonding, and Zs read 3.5Ω at a socket next to the rewireable fuse box!