Been testing at Secure Heights today....
My Zs's are all up the creek. Not tried lighting, but rings & cooker circuits are much higher than the adjusted figures I use.
Ze is 0.22 on TN-S.
But Zs from rings are: 1.37, 1.46 & from cooker 1.05.
One ring continuity test reads L = 0.54 N = 0.54 E=0.95
Rings & cooker on 32A Type 2's.
Initially thought Ze was up the creek, but it seems all these 3 circuits are much higher than the max allowable, especially taking into account the low Ze.
Cooker circuit is 8m away. Rings may be majority 2.5/1.0, though.
I fear I have a few too many JB's with loose connections. All connections are tight at CU & outlets.
Inherited the system when house purchased in 1999. Time for a rewire, methinks...