Let me guess, It's a metalclad switchfuse in your meterbox?
If PME earthing is available on your supply, then it's best to have the upgrade, and will save a lot of work for you too. You will however have to ensure that main earthing and protective bonding conductors are big enough for the new earthing system.
If PME is not available and you have to stick with TT, your best bet is to install a mini PLASTIC CU in your meterbox, with the armoured terminated into it and the gland / armour earthed with a piranah nut or similar.
In the CU terminate the meter tails direct into a 100mA type S RCD, which in turn supplies a type C 63A MCB to feed the submains to your house CU.
This same RCD can also cover the new T&E submains too by supplying it from an MCB in your house CU. Something like a 50A MCB would be ideal to provide discrimination from the 63A MCB in the meter cabinet.
Then RCD protect all the other circuits with 30mA non time delayed RCDs. Either a dual split type CU or each circuit protected by a DP RCBO.
If PME earthing is available on your supply, then it's best to have the upgrade, and will save a lot of work for you too. You will however have to ensure that main earthing and protective bonding conductors are big enough for the new earthing system.
If PME is not available and you have to stick with TT, your best bet is to install a mini PLASTIC CU in your meterbox, with the armoured terminated into it and the gland / armour earthed with a piranah nut or similar.
In the CU terminate the meter tails direct into a 100mA type S RCD, which in turn supplies a type C 63A MCB to feed the submains to your house CU.
This same RCD can also cover the new T&E submains too by supplying it from an MCB in your house CU. Something like a 50A MCB would be ideal to provide discrimination from the 63A MCB in the meter cabinet.
Then RCD protect all the other circuits with 30mA non time delayed RCDs. Either a dual split type CU or each circuit protected by a DP RCBO.