This is a list of the changes between the 17th edition and the new 18th DPC, numbered in the order that they appear in the document.
The DPC is now available for download as a PDF file, which is much easier to use and can be searched through, unlike the online system. Download from the same place as the online version.
Part 2 new definitions:
Combined short circuit current capability
Combined short circuit protection
Conditional short circuit current
Continuity of service
Control and protective switching device
Co-ordination of electrical equipment
Departure
Energy efficiency
Foundation earth electrode
Inland navigation vessel
Non-compliance
Overcurrent protective device
Partial selectivity
Short circuit current rating
Short circuit protective device
Part 4
411.3.1.2 NEW - Metallic pipes entering the building having an insulating section at their point of entry need not be connected to the protective equipotential bonding
411.3.2.1 Additions re. device suitable for isolation of at least the line conductor, new Note re. IT systems on 1st/2nd fault disconnections
411.3.2.2 Additionally applies to 63A with 1+ socket outlet
Table 41.1 Disconnection time for DC 120-230V changed (was 5, now 1)
Note 2 New note, disconnection provided by RCD, refers 411.4.4 411.5.3 411.6.5
411.3.2.5 Wording changed completely
411.3.2.6 Deleted, automatic disconnection/supplementary bonding. See new 419.
411.3.3 Exceptions for no RCD on socket outlets deleted, all socket outlets now require RCD
411.4.2 Note changed from 'may additionally be connected ..' to a reference to 542.1.201 which now requires connection to an earth electrode in TN systems
411.4.3 Added 'no switching or isolating device shall be inserted in the PEN conductor'
411.4.4 Previously content in 411.4.5. New Note 2, fault currents in TN systems when RCDs used
411.4.5 Previously content in 411.4.4 Amended ref 531.2.9 > 536.4.1.6. Changed 'discrimination' to 'selectivity'.
411.4.201 Previously content in 411.4.6
411.4.203 Previosuly content in 411.4.8
411.4.204 Previously content in 411.4.9
411.5.1 Additional text re. neutral point/mid point being earthed.
411.6.1 Some rewording, new Note 2
411.6.2 No longer applies to DC systems, note explains why
411.6.3 2 new Notes, RCD capacitive leakage, and faults in different devices
411.6.3.1 Deleted - see new 411.6.4
411.6.3.2 Deleted - see new 411.6.4
411.6.4 Various changes, some content from 411.6.3.1/2 included here
411.6.5 Various changes to layout, notes, etc
412.1.2 Content from 412.1.3 with revisions
412.1.3 Deleted - most content now in 412.1.2
413.3.3 Minor change to text, meaning unchanged
414.1.2 Minor change to note, locations -> cases
414.4.5 (iii) and (iv) are now (i) and (ii) after 'basic protection is generally..'
415.2.2 Lines now numbered (i) and (ii), previously not numbered. Minor change to text, meaning unchanged
419 All new, provisions where automatic disconnection is not feasible (also ref old deleted 411.3.2.6)
421.1.7 New - arc fault detection devices may be used
422.2.1 'wiring systems in escape routes as short as possible' deleted. Changes - other standards for cable, add euroclasses for reaction to fire, smoke production, etc.
422.3.4 change to ref. euroclass eca standards, various other minor changes to standards for cables etc.
422.4.203 changed from comply with BSEN60332-1-2 to comply with 422.2.1
440.2 Content now in a table, content unchanged
443 All significantly rewritten and expanded, substantial new content, plus annexes
46 Isolation and Switching All new. Similar content was in previous 16th edition. Also see 53
The DPC is now available for download as a PDF file, which is much easier to use and can be searched through, unlike the online system. Download from the same place as the online version.
Part 2 new definitions:
Combined short circuit current capability
Combined short circuit protection
Conditional short circuit current
Continuity of service
Control and protective switching device
Co-ordination of electrical equipment
Departure
Energy efficiency
Foundation earth electrode
Inland navigation vessel
Non-compliance
Overcurrent protective device
Partial selectivity
Short circuit current rating
Short circuit protective device
Part 4
411.3.1.2 NEW - Metallic pipes entering the building having an insulating section at their point of entry need not be connected to the protective equipotential bonding
411.3.2.1 Additions re. device suitable for isolation of at least the line conductor, new Note re. IT systems on 1st/2nd fault disconnections
411.3.2.2 Additionally applies to 63A with 1+ socket outlet
Table 41.1 Disconnection time for DC 120-230V changed (was 5, now 1)
Note 2 New note, disconnection provided by RCD, refers 411.4.4 411.5.3 411.6.5
411.3.2.5 Wording changed completely
411.3.2.6 Deleted, automatic disconnection/supplementary bonding. See new 419.
411.3.3 Exceptions for no RCD on socket outlets deleted, all socket outlets now require RCD
411.4.2 Note changed from 'may additionally be connected ..' to a reference to 542.1.201 which now requires connection to an earth electrode in TN systems
411.4.3 Added 'no switching or isolating device shall be inserted in the PEN conductor'
411.4.4 Previously content in 411.4.5. New Note 2, fault currents in TN systems when RCDs used
411.4.5 Previously content in 411.4.4 Amended ref 531.2.9 > 536.4.1.6. Changed 'discrimination' to 'selectivity'.
411.4.201 Previously content in 411.4.6
411.4.203 Previosuly content in 411.4.8
411.4.204 Previously content in 411.4.9
411.5.1 Additional text re. neutral point/mid point being earthed.
411.6.1 Some rewording, new Note 2
411.6.2 No longer applies to DC systems, note explains why
411.6.3 2 new Notes, RCD capacitive leakage, and faults in different devices
411.6.3.1 Deleted - see new 411.6.4
411.6.3.2 Deleted - see new 411.6.4
411.6.4 Various changes, some content from 411.6.3.1/2 included here
411.6.5 Various changes to layout, notes, etc
412.1.2 Content from 412.1.3 with revisions
412.1.3 Deleted - most content now in 412.1.2
413.3.3 Minor change to text, meaning unchanged
414.1.2 Minor change to note, locations -> cases
414.4.5 (iii) and (iv) are now (i) and (ii) after 'basic protection is generally..'
415.2.2 Lines now numbered (i) and (ii), previously not numbered. Minor change to text, meaning unchanged
419 All new, provisions where automatic disconnection is not feasible (also ref old deleted 411.3.2.6)
421.1.7 New - arc fault detection devices may be used
422.2.1 'wiring systems in escape routes as short as possible' deleted. Changes - other standards for cable, add euroclasses for reaction to fire, smoke production, etc.
422.3.4 change to ref. euroclass eca standards, various other minor changes to standards for cables etc.
422.4.203 changed from comply with BSEN60332-1-2 to comply with 422.2.1
440.2 Content now in a table, content unchanged
443 All significantly rewritten and expanded, substantial new content, plus annexes
46 Isolation and Switching All new. Similar content was in previous 16th edition. Also see 53