... No I didn't reference the RCBO standard to deceive, just that they're both very similar ...
I certainly didn't accuse you of attempting to 'deceive', and nor do I think anyone else did. I thought you'd probably made a mistake, aided by the fact that (as BAS said), this thread is a spin-off from one about RCBOs. ... The standards may be similar but, at least in the past, there has seemingly been a significant difference between the devices. Maybe it's down to lack of exposure/experience, but I've never seen or heard of an RCBO in which the residual currenmt part was not electronic, whereas, at least in the past (I'm not so sure any more) at least some RCDs did not use any electronics.
... and I'm sure a majority of residual current measuring devices installed by electricians are now contained within RCBO units.
I'm not sure I understand that, or its relevance.
The functional descriptions of 4.1.2.2a (E1) and 4.1.2.2b (E3) appear to be identical,
Typo now corrected
Thanks.
Does the standard clarify what is meant by “Able to trip under hazardous circumstances (e.g. earth fault) arising due to failure of line voltage”. Is this perhaps merely a reference to the fact that (given a low enough Zs) the overcurrent part (which probably does not involve any electronics) (but not the ‘RCD part’) will operate in response to a L-E fault even if there is no supply voltage, or does it mean something different or more complicated than that. In particular, does anything in the Standard indicate whether the ‘RCD part’ of the devices concerned (E1 and E3) still works when there is no power?
The RCD descriptions are identical in both standards BS EN 61008-1 and BS EN 61009-1, so the only things which are dependant on voltage are the RCD elements. I can't imagine why the MCB elements would be dependant on voltage being present.
Nor can I, and I wasn't suggesting that it would.
Again, after checking the wording is actually "on failure of line voltage" but it doesn't really make the statement any clearer, and I would imagine the former would cause the latter, but the statement implies otherwise, which is naturally a worst case insofar as the RCDs functionality but not one I've encountered.
Quite. The statement is so confused/confusing that I think we simply have to ignore it for the time being! As you say, what on earth could be meant by "earth fault arising due to [or on] failure of line voltage"?!! My question therefore must essentially remain unanswered.
Do I take it that (although this would make one of them redundant) “Provide service continuity” actually means the same as “Not opening automatically if line voltage lost”? If not, does the Standard indicates what it does mean?
It just has "Service Continuity" with Yes or No in the table, with a footnote of "This information is given for guidance only" and nothing in the definitions.
The more one hears about this document, the worse it gets!
Given the fact that it has ‘no marking’ and a different section number, one suspects that 4.1.1 probably refers to ‘ordinary/common’ RCBOs but, ironically, few details about this one have been provided – is any more available?
That marking is, I quote: .....
I wasn't asking for more details of the marking
I was noting that there is far less functional information about this class of device than about the other three, and therefore wondered if anymore (functional) details were available.
Is there any explanation of the meaning of “Function independent on (s.i.c.) line voltage”, since this is really the issue we’ve been discussing. In particular, does it really mean that the ‘RCD functionality’ will still work even if the L-N pd seen by the RCD falls to zero or near zero?
Yes, in the definitions of both standards: "RCCBs/RCBOs for which the functions of detection, evaluation and interruption do not depend on the line voltage"
That seems essentially to be 'defining' the phrase by paraphrasing it
I suppose your answer is bound to be 'yes', but what I was asking is whether 'not dependent on line voltage' really does mean that it still works if line voltage falls to zero. If so, I still don't understand how it can work if the device has and electronic+solenoid mechanism of operation.
In any event, as my subsequent post said, after further consideration, I've come to the conclusion that we're probably discussing a non-problem. The L-N voltage seen by the device could only fall to near zero in the case of an L-CPC fault very close to the RCD in a TN-C-S system, in which case an OPD (even if the cutout fuse) would virtually always operate. In all other situations, plenty of voltage would remain across the RCD for the electronics etc. to work.
Kind Regards, John