I was really asking about what sort of 'metal' you had in mind - are you talking about the metal enclosure of something (an isolator or switchfuse, perhaps?) upstream of any other RCD protection?...that any metal has to have a minimum of 100ma rcd protection on a TT earth. Not sure how to explain...
Kind Regards, John
Yes, as the supply into the garage won't be rcd protected, any exposed metal parts before the cu rcd must have min 100ma on TT.
Which can be avoided by using plastic boxes and cu.
Again, think I'm right on this.