I don't know how you've done your anchors, so I'll put down the most detailed esplanation I camn of how I use them. Bear in mind that a lot of the resins I put in are inmto ropey Victorian or Georgian brickwork where we might only get one decent fix for every three holes - in modern masonry you should get almost every one spot on. I've included a fault finder below that
The way you I resin anchors is to drill the holes (2mm bigger than the stud, no more), blow out, brush out or vacuum out any drilling debris, then inject the resin - starting with the mixer nozzle full in gto the shouldet of the nozzle pumping and withdrawing the gun gently (the idea is to almost completely fill the hole but not drop any resin into voids or cavities - with the guns we use that is about 3 to 5 pumps) then slowly insert the threaded stud V-shaped end first whilst turning slowly (you are effectively screwing the stud into the resin, making sure that the threads get a good purchase on the resin). Put the washer(s) and nuts on, but leave everything loose until the resin sets hard (20 to 60 minutes depending on temperature and resin type). This is another reason why I put the temporary support blocks on the wall and why I often use a few brown plugs and 5 x 100 mm screws to hold the ledger in place until the resin sets. Once the resin has set, tighten the nuts to hand tight, no more - don't tighten until the resin is
fully cured (often 12 to 24 hours, especially in winter ). Some stud suppliers, such as Hilti, machine a square on the ends of their studs so that you can do the first tightening before the resin is cured by holding onto the stud with an OE wrench. when the resin has fully cutred revisit the nuts and fully tighten with a wrench or ratchet - they should all tighten fully, but invariably some won't (at least in old brickwork or soft masonry). How many do you have and how many are suspect?
Some reasons why studs won't tighten (not comprehensive, but everything I can think of at the moment):
1. Hole still contains debris (not cleaned out thoroughly) leading to poor adhesion between resin and masonry
2. Hole drilled too large (needs more resin)
3. Insufficient resin injected
4. Stud threads not bedded into resin (pushed in as opposed to screwed in)
5. Resin pushed out of hole and into a void cavity because stud insertion too vigorous (go slower and screew in stud)
6. Hole drilled into mortar or invisible void in masonry
7. Attempt to fully tighten before the resin is completely cured