You would have thought the outdoor socket would be on a 16a
I can change the mcb if required to but at the moment it fine
You would have thought the outdoor socket would be on a 16a
You would accept a neon on a 45a switch ? i.e. shower, cooker whats the difference the 40a mcb protects the cable, apparently.Maybe pedantic, but Not sure how others feel about one of the Neons and its (short) possibly underated wiring, backed up by a 40 amp mcb though
Do you mean the "main power in" neon
You would accept a neon on a 45a switch ? i.e. shower, cooker whats the difference the 40a mcb protects the cable, apparently.Maybe pedantic, but Not sure how others feel about one of the Neons and its (short) possibly underated wiring, backed up by a 40 amp mcb though
Do you mean the "main power in" neon
Regards,
DS
You would accept a neon on a 45a switch ? i.e. shower, cooker whats the difference the 40a mcb protects the cable, apparently.Maybe pedantic, but Not sure how others feel about one of the Neons and its (short) possibly underated wiring, backed up by a 40 amp mcb though
Do you mean the "main power in" neon
Regards,
DS
They would be part of the switch accesory and such accesory normally supplied by a cable fused and capable of carrying 45 amp.
What cable csa would you assume most likely to be between the shed Cu rcd and that indicater labelled supply in and what size would you expect to conform to regs
Hold fire and see what others say, as I said i may be being a bit pedantic
What may help is if one day you could ISOLATE the switch in the house and get a picture of INSIDE the Shed CU.
Aside from that indicater
The other 3, as they are on there own MCB's they should have 3 seperate neutrals
An internal photo of the shed CU will reveal all
But ISOLATE at house first
There not major problems but seeing as you asked if the install was ok, they are things to bear in mind.
rather than an inline fuse a suitable CSA cable to that neon may be a cheaper
alternative
It may just be easier to remove the whole neon setup.
I think you probably are (being a bit pedantic) . As discussed in the past, even a pretty small cable/conductor (which it probably is) would probably get adequate fault protection from a 40A OPD, and I can't for the life of me see how a neon is going to create an overload (as opposed to fault) situation.Hold fire and see what others say, as I said i may be being a bit pedantic
Indeed, that's what I said (or, at least, implied!) in the previous post. As I also said, per discussions (and calculations) we had a little while ago, a 'surprisingly small' cable gets adequate fault protection from a 40A MCB (IIRC, the calculations I did were for a 50A one) - so it's likely that, even if one is being 'pedantic', what the OP has is probably OK. I'll see if I can find the figures.The cable needs no overload protection. It needs fault protection. You need to decided/determine if it does.
Found ....Indeed, that's what I said (or, at least, implied!) in the previous post. As I also said, per discussions (and calculations) we had a little while ago, a 'surprisingly small' cable gets adequate fault protection from a 40A MCB (IIRC, the calculations I did were for a 50A one) - so it's likely that, even if one is being 'pedantic', what the OP has is probably OK. I'll see if I can find the figures.The cable needs no overload protection. It needs fault protection. You need to decided/determine if it does.