I like to waste resources and earth both ends of the armour when I can, because it's belt, braces
Or there just isn't room for a 25mm gland....Usually there is only one reason to use the seperate box - and that is because the consumer unit is plastic.
If the CU is metal then you've got no choice at that end.I like to waste resources and earth both ends of the armour when I can, because it's belt, braces and two condoms.
I like to waste resources and earth both ends of the armour when I can, because it's belt, braces .
If the CU is metal then you've got no choice at that end.
True, if it is.Metal CU at the far end may have to be isolated from the armouring if the far end is TT ( no exported earth permitted )
.. it's TN-S.
If the supply bis TN-S then I agree that most, if not all, of the theoretical hazards which lead some people to favour TTing an outbuilding cease to exist.Probably no good reason for that, though:
True, but I think it could probably still be more than would be provided by small-CSA SWA.If it is truly TN-S then large bonding conductors are not required.
In true TN-S the bonding conductor doesn't have to be run back to the MET.; just installed in the out building.True, but I think it could probably still be more than would be provided by small-CSA SWA.
I don't have access to regs etc. at the moment, but do they really say that?In true TN-S the bonding conductor doesn't have to be run back to the MET.; just installed in the out building.
I'm getting confused here. Isn't the "earthing conductor" just the conductor between the supplied earth (DNO TN earth or local electrode) and the MET? In any event, a (non-PME) main bonding conductor is, as you say, required to be at least half the CSA of the required earthing conductor but with a minimum of 6mm², and I have always taken that to relate to a copper conductor - is that not correct? If I am right, does, say, 2-core 2.5mm² SWA have an armour with a copper-equivalent CSA of at least 6mm² ?In the out building, it just has to be half the csa of the required earthing conductor, so the earthing conductor back to the house is used.
Well they may not actually say that but that is the outcome.I don't have access to regs etc. at the moment, but do they really say that?
Yes, sorry, I should have said CPC - although it will be the earthing conductor for the out-building, won't it?I'm getting confused here. Isn't the "earthing conductor" just the conductor between the supplied earth (DNO TN earth or local electrode) and the MET?
It is correct.In any event, a (non-PME) main bonding conductor is, as you say, required to be at least half the CSA of the required earthing conductor but with a minimum of 6mm², and I have always taken that to relate to a copper conductor - is that not correct?
I haven't looked it up, but if a 2.5mm² CPC (earthing conductor) is adequate for the supply in the out building then the equivalent of 1.25mm² is likely - if it needs to be used instead or as well as the CPC (EC).If I am right, does, say, 2-core 2.5mm² SWA have an armour with a copper-equivalent CSA of at least 6mm² ?