Who knows - but I suspect that the minimum may well be in relation to 'mechanical ruggedness', much as maybe also the reason for the minimum for a single CPC being 4mm².Well they may not actually say that but that is the outcome.
As in the house, the earthing conductor is sized by the adiabatic equation and bonding conductors half of that - subject to the minimum, of course - but is that for electrical reasons?.
I wouldn't have thought so - unless you're going to suggest that the outbuilding is a separate installation (!!) (with it's own MET). As I said, I have always thought that the 'earthing conductor is only/just the conductor from the earth (TN or local electrode) to the MET, and I presume that one installation can only have one MET (the clue being the 'M').Yes, sorry, I should have said CPC - although it will be the earthing conductor for the out-building, won't it?
I would have thought that there would still be a minimum CSA for whatever material was being used, that minimum being equivalent to 6mm² of copper - in other words, if the minimum for copper is 6mm², the minimum for steel would presumably be a lot greater than 6mm².It is correct. However, if a bonding conductor of, say 3mm², were all that were actually required (apart from the minimum specification) then, surely a copper equivalent of that would be required; not the 6mm² minimum.
You seem to again be assuming that the CPC to the outbuilding can be regarded as an 'earthing conductor' and that a bonding conductor is therefore only required to have a CPC of half the CSA of that CPC, rather than half of the required CSA of the (house's) installation's true earthing conductor (from DNO/rod earth to the {house's} MET). I'm not at all sure that one can make those assumptions.I haven't looked it up, but if a 2.5mm² CPC (earthing conductor) is adequate for the supply in the out building then the equivalent of 1.25mm² is likely - if it needs to be used instead or as well as the CPC (EC).
Kind Regards, John