Cable type and installation method means a set size of cable has a massive range of amps rating.
As well as the amp rating we also have if the loop impedance it low enough to ensure the magnetic part of the overload will work, and the permitted volt drop is not exceeded.
So with a B32 MCB for example the magnetic part needs 5 times the current to trip to the thermal part of the trip, plus 5% allowance for volt drop, so (230/(32 x 5)) x 95% = 1.365625Ω the supply also has some loop impedance typical 0.35Ω so around one ohm for the cable.
As electricians we tend to estimate what the impedance will be, and only actually calculate when we realise we are getting close to the limit. I find the calculations are a bit of a pain, and so made myself a program to calculate it for me, which means less likely to make an error.
The hope is when it comes to actually measure the loop impedance it is within limits. Although once installed and the installation certificate has been completed there is no requirement to code if the volt drop is exceeded when doing an EICR so in real terms there are only a few appliances where volt drop is important.
Fluorescent lights with wire wound ballast and refrigeration are very voltage dependent, but little else.
Even twin and earth comes as thermal setting and thermal plastic 90°C or 70°C and we tend to use installation methods 100 to 103 so a 4 mm² cable could be between 17.5 amp and 27 amp and moving to method C 37 amp.
But at the end of the day the person who signs the installation certificate has to decide what is used and how it is run, and I don't think if I came to do a job and the customer tried to tell me my job, I would not take it kindly, so you need to consider what to say to the electrician.