yes and no..
you can either use a bit of flexible conduit or something similar ( blue water pipe etc.. or you can bury it in the concrete.. ..
you'll need an inspection pit outside and an earth rod.. best your sparky gives you the details.. liasing with him now before the build starts is a good idea to see what he wants done..
Sorry I forgot to mention the earth pit. I dont do much domestic installation nowadays. Its all part of the wiring regulations. If you are doing the job yourself ensure that the garage end of the SWA is insulated (assuming you are PME) and nothing can come into contact with it. Dont even attach it to your wiring enclosure, or C/U if they are metalic. The enclosures should be of PVC form anyway if my memory serves me correct. I used to put heatshrink sleeve over the armour where it was cut off to expose the inner flex, some would use insulation tape. I think the earth cable between the garage c/u and earth pit is a minimum of 10mm but for mechanical reasons it is best to use 16mm earth cable. Any how the RCD test has to be carried out on the installation and you will need a loop impedance meter and an RCD tester so unless you are a qualified bod you won't have these items. Make sure your sparky gives you some form of test certificate because this work is notifiable and when you come to sell the house this peice of paper will be required. Not that anybody looking at it will understand it of course..lol