Not going to happen.what would you say if it were a 2-core cable which was 'mechanically protected' (but not by earthed metal)
411.3.1.1
A circuit protective conductor shall be run to and terminated at each point in wiring and at each accessory except a
lampholder having no exposed-conductive-parts and suspended from such a point.
A submain is not a lampholder.
CPC is required regardless of whether it is connected at the load or not.
If the SWA isn't connected to a suitable gland, the CPC cannot be properly terminated.