Hi
Thanks Kendor for your input.
To [hopefully] conclude this matter, I did the following experiment which I believe
adequately explains my 91V issue and the energy saving light.
I took 3 metres of 1mm^2 twin and earth switch cable, and lay it on my floor.
I then connected on one end of it a light holder (ceiling rose type) and left it
empty (no bulb in it)
I then connected the other end of the cable as folllows.
The earth wire was connected to my house electrics earth and the
LIVE wire (red) to my house electrics LIVE wire. The black wire of this
cable was left disconnected at BOTH ends.
I then measured the p.d. beween the black and earth wire at the light holder
end and my meter displayed 29V. (It also read 242V between the red wire
and earth.) My meter is a Fluke 8020B, set to range 750V, A.C.
So, in 3m of this cable one can expect to *see* about 30Volts induced
in a free/floating disconnected [black] wire that is running parallel inside the cable
very closely next to the red wire which has a potential of 242V on it (not loaded)
So, for a longer switch cable, e.g. in my 2-way circuit, I conclude that 61V is
typical, and when both switches are switched off in the other direction, as two wires
then are at LIVE voltage, there is more indcued in the floating wire and one sees
91V as I did.
Of course, there would be negligible current flowing if one measured it between
the black floating wire and earth, as I did and saw 0.04 milliAmps. So this is not
a hazard, I would suggest.
I hope this info is helpful to others (and boy I wish I could have read this in a book
somewhere.)
Thanks again to all.
Tricia