There is a difference between what the BSI/IET regulations allow and what is safe some common sense needs to be used.
The regulation says that any buried cable in wall or ceiling less than 50mm from surface (which means most cables since running cables through cavities no longer allowed) must be either special cables complying with BS 5467, BS 6346. BS 6724, BS 7846, BS EN 60702-1 or BS 8436 or be RCD protected with a 30ma non delayed RCD.
So in theory the cable to the outside socket needs to be one of the specials or the RCD fitted at origin i.e. using a RCD FCU. The idea is should some one drill or nail into the wall and hit cable they will not be electrocuted although they would likely get a shock.
These rules came in 2008 but not retrospective.
The regulation says that any buried cable in wall or ceiling less than 50mm from surface (which means most cables since running cables through cavities no longer allowed) must be either special cables complying with BS 5467, BS 6346. BS 6724, BS 7846, BS EN 60702-1 or BS 8436 or be RCD protected with a 30ma non delayed RCD.
So in theory the cable to the outside socket needs to be one of the specials or the RCD fitted at origin i.e. using a RCD FCU. The idea is should some one drill or nail into the wall and hit cable they will not be electrocuted although they would likely get a shock.
These rules came in 2008 but not retrospective.