Table 41.1 and Reg 411.3.2.2

Joined
29 Jun 2006
Messages
396
Reaction score
20
Location
Middlesbrough
Country
United Kingdom
Ayup chaps,

Would you be bale to confirm this for me please?

Quoting the red bible.

411.3.2.2 - (Table 41.1 TN system) Any final circuit at 230v not exceeding 32A must disconnect in 0.4s.
411.3.2.3 A TN circuit can disconnect upto 5s as long as it is a distribution circuit or exceeds 32A.


Therefore.. does the 17th no longer recognise fixed equipment/ portable equipment? That being said.. lighting circuits now have to diconnect in 0.4 seconds?

confused.com :confused: :confused:
 
Sponsored Links
Ayup chaps,
Therefore.. does the 17th no longer recognise fixed equipment/ portable equipment? That being said.. lighting circuits now have to diconnect in 0.4 seconds?

Well it is true to say that it no longer uses those distinctions for this aspect of shock protection.

This is a significant improvement because it removes the (hard to defend) situation where a portable hand held appliance would have to disconnect within 0.4 seconds, but a hand gripped fixed appliance (a lathe for example) would not. However, the decline in the use of fuses for final circuits has done much to make these distinction irrelevant in most installations.
 
Sponsored Links
I repeat - the nominal supply voltage in the UK is 230 volts.

This is a matter of European harmonisation - it would breach an EU Directive if it were not.

Look here under amendment 4

http://www.opsi.gov.uk/si/si1994/Uksi_19943021_en_1.htm

Now the voltage at your house could be 240V or even 250V that does not matter - the nominal voltage is 230V.
 
Yeah, I am assuming we are still required to use the 230 column hence, 0.4s.

Well... this could mean having to put lighting circuits, immersion heaters and fused spur radial circuits on RCDs to achieve the 40ms trip time?
 
Assuming you are using type B or C MCBs .4s vs 5s disconnect time will make virtually no difference at all. To get under 5s you need to hit the fast trip and once you hit the fast trip the MCB will disconnect extremely quickly (.1s iirc)
 
I think what Gareth might be getting at is or i am getting at is what is the use of table 41.4 for the 6A thru 32A columns.
 
Aye, that's what I was thinking.. but then you could supply a 2 way unit for a couple of daft lighting circuits off a 6 amp fuse I suppose?
Then that being classed as a distribution circuit it can take upto 5s to trip.
 
TF2 :O I've seen the vids.. looks like fun. :cool: I am CS 1.6 all the way though dude. (Head admin of britishsergeantsmess.com):cool:
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Sponsored Links
Back
Top