I went to a house today and a spark has fitted and notified a new c/u and told the owners that they need a rewire. They have all pvc cable from what I can see.
His paperwork consists of an EIC and Schedule of test, but no Schedule of inspections which is wrong according to page 87 of GN3 paragraph 2.
He states 16mm earthing conductor but has only fitted 10mm
He states 6mm main bonding conductors when there is only a 4mm one to the gas and no bond at all on the water services.
He has put in the observation section that there is a n/e fault on the lighting circuit. A broken ring on down sockets (but has still fitted a 32A mcb) and there is no CPC continuity on some light fittings (no warning on CU)
No harmonised colour warning and no retest label of RCD one.
What to do about him>?
I have told them I would do a PIR before anything else and go from there but my initial assessment is that there is no need for a full rewire and the huge upheaval it would involve for them
I wonder if they will go back to him, I know I would.
If I don't get the job and he say he will put it all right and it does need a rewire I shall be peeved.
Martin
His paperwork consists of an EIC and Schedule of test, but no Schedule of inspections which is wrong according to page 87 of GN3 paragraph 2.
He states 16mm earthing conductor but has only fitted 10mm
He states 6mm main bonding conductors when there is only a 4mm one to the gas and no bond at all on the water services.
He has put in the observation section that there is a n/e fault on the lighting circuit. A broken ring on down sockets (but has still fitted a 32A mcb) and there is no CPC continuity on some light fittings (no warning on CU)
No harmonised colour warning and no retest label of RCD one.
What to do about him>?
I have told them I would do a PIR before anything else and go from there but my initial assessment is that there is no need for a full rewire and the huge upheaval it would involve for them
I wonder if they will go back to him, I know I would.
If I don't get the job and he say he will put it all right and it does need a rewire I shall be peeved.
Martin