thanks Dan, I inherited this system so I didn't really have a choice.
From what you said in a previous post.
The boiler must have feedback to tell it to go in to cycling off mode. If I reduce the flow temperature thermostat on the front of the boiler, it will go in to this cycling mode. I don't think its the thermostat on the thermal store thats telling it. From reading around it looks like the boiler monitors the flow return coming back from the thermal store. If the temp is not that much lower than it was sent out at then the boiler thinks the store is coming up to temp and so starts to throttle back.
If this is what is happening then I guess it could be a number of things related to this.
1) poor transfer of heat from boiler coil inside thermal store. This is what Dan said. Scale??? but I live in a soft water area.
2) Broken thermistor on flow return side?
3) Broken thermistor on flow source side? I can check with a mulitmeter.
Could the thermistor on the flow return side be disconncted and just run off of the thermostat on the thermal store which can switch off the boiler.
I think we are getting there
C
From what you said in a previous post.
If it is cycling before the store is up to temperature then there is poor heat transfer through the system between store and boiler.
The boiler must have feedback to tell it to go in to cycling off mode. If I reduce the flow temperature thermostat on the front of the boiler, it will go in to this cycling mode. I don't think its the thermostat on the thermal store thats telling it. From reading around it looks like the boiler monitors the flow return coming back from the thermal store. If the temp is not that much lower than it was sent out at then the boiler thinks the store is coming up to temp and so starts to throttle back.
If this is what is happening then I guess it could be a number of things related to this.
1) poor transfer of heat from boiler coil inside thermal store. This is what Dan said. Scale??? but I live in a soft water area.
2) Broken thermistor on flow return side?
3) Broken thermistor on flow source side? I can check with a mulitmeter.
Could the thermistor on the flow return side be disconncted and just run off of the thermostat on the thermal store which can switch off the boiler.
I think we are getting there
C