You may have read, a week or two ago, I bought a pair of cheap digital temperature displays, with remote sensors, displaying with an accuracy to 0.1C, with the intention of utilising them as pipe thermometers.
After a while assessing there accuracy - they are spot on, I have clipped them on the flow and return of my boiler, using pipe insulation. What I've noticed since my Vaillant system was installed, is that the boiler display almost always shows several degrees above ambient [1], even when it has been several hours since there was last a call for heat. I have a OV cylinder, and a MOMO 3-port valve. MOMO leaves the valve setting at what ever position it was last called to serve - HW or CH.
I am not at the moment needing to run the boiler for space heating, it only needs to fire up to maintain the HW in the cylinder. Triggering the heating, to increase the room temperature, thanks to my fancy Vaillant predicted control system, the flow temperature only hits 34C, prior to shutting off, with a return of 27C. Which seems fine.
With the boiler cold, having last served HW, there is a temperature difference across the boiler of around 5C, due to the thermo.
Thanks to the temperature displays, I think I have now worked out the reason for [1] above - thermo-syphoning. If the MOMO stops having just served the heating of the cylinder, the valve will remain open to the coils in the cylinder. Once the boiler shuts down, thermo-syphoning, will take effect, circulating heat back from the cylinder, down to the boiler, and cold air around the boiler's heat exchanger, will dissipate that heat.
It's not necessarily a problem just of MOMO type valves, because even the spring returns default to being open to the cylinder, when there is no call for heat. At least if there is a call for CH a MOMO will remain set for CH, until the next call for HW.
After a while assessing there accuracy - they are spot on, I have clipped them on the flow and return of my boiler, using pipe insulation. What I've noticed since my Vaillant system was installed, is that the boiler display almost always shows several degrees above ambient [1], even when it has been several hours since there was last a call for heat. I have a OV cylinder, and a MOMO 3-port valve. MOMO leaves the valve setting at what ever position it was last called to serve - HW or CH.
I am not at the moment needing to run the boiler for space heating, it only needs to fire up to maintain the HW in the cylinder. Triggering the heating, to increase the room temperature, thanks to my fancy Vaillant predicted control system, the flow temperature only hits 34C, prior to shutting off, with a return of 27C. Which seems fine.
With the boiler cold, having last served HW, there is a temperature difference across the boiler of around 5C, due to the thermo.
Thanks to the temperature displays, I think I have now worked out the reason for [1] above - thermo-syphoning. If the MOMO stops having just served the heating of the cylinder, the valve will remain open to the coils in the cylinder. Once the boiler shuts down, thermo-syphoning, will take effect, circulating heat back from the cylinder, down to the boiler, and cold air around the boiler's heat exchanger, will dissipate that heat.
It's not necessarily a problem just of MOMO type valves, because even the spring returns default to being open to the cylinder, when there is no call for heat. At least if there is a call for CH a MOMO will remain set for CH, until the next call for HW.