Yes, it is.I'm just wondering if that's the only option right now?
Yes, it is.I'm just wondering if that's the only option right now?
It seems fairly unlikely that the DNO-supplied earth is significantly 'high resistance'. A TN-S earth is allowed to have a Ze of up to 0.8Ω - so, unless the cooker circuit is pretty short in length, the measured Ze of 1.19Ω would seem to be quite credible(if the Ze of the DNO earth was close to the 'maximum allowed).I called UKPN - went as well as I expected. They just redirected me to the form I already told them I'd seen. Computer says no.
I was going by another response suggesting I just contact the DNO.It seems fairly unlikely that the DNO-supplied earth is significantly 'high resistance'. A TN-S earth is allowed to have a Ze of up to 0.8Ω - so, unless the cooker circuit is pretty short in length, the measured Ze of 1.19Ω would seem to be quite credible(if the Ze of the DNO earth was close to the 'maximum allowed).
Only if the length of the cable from CU to hob is pretty short. Of course,the Ze may bee nowhere near as high as 0.8Ω - that is the theoretical 'maximum'The hob installer said only 0.87Ω would be acceptable at the hob connection - so if you're saying 0.8Ω would be ok for Ze, is just 0.07Ω realistically achievable for the connection from CU to hob?
In which case I'm not sure where that leaves me - are the installers wrong to not install? Or do 32A hobs just have to be really close to the CU?Only if the length of the cable from CU to hob is pretty short. Of course,the Ze may bee nowhere near as high as 0.8Ω - that is the theoretical 'maximum'
You need an electrician.In which case I'm not sure where that leaves me -
No.are the installers wrong to not install?
No.Or do 32A hobs just have to be really close to the CU?
They're not really 'wrong', in that any use of the circuit is theoretically 'not safe' if the Zs is too high.In which case I'm not sure where that leaves me - are the installers wrong to not install?....
That obviously depends on Ze. With TN-C-S the 'maximum'; is 0.35Ω and, in practice, may well be a lot lower than that-so the situation is therefore then much more manageable. People who sell fairly high-powered electrical appliances don't seem to 'warn' customeers about the potential issues of suitability of their electricity supply..... Or do 32A hobs just have to be really close to the CU?
But you're saying the DNO can legally leave me in a situation where Ze is 0.8Ω, and therefore mean I can't practically/within safety limits have an induction hob, unless I move my kitchen or CU?They're not really 'wrong', in that any use of the circuit is theoretically 'not safe' if the Zs is too high.
That obviously depends on Ze. With TN-C-S the 'maximum'; is 0.35Ω and, in practice, may well be a lot lower than that-so the situation is therefore then much more manageable.
IndeedBut you're saying the DNO can legally leave me in a situation where Ze is 0.8Ω, ...
Even moving your CU would not help, since it's the total cable run back to the DNO's transformer that determines Zsand therefore mean I can't practically/within safety limits have an induction hob, unless I move my kitchen or CU?
I understand your frustration,but that's how it is. As I've just written,no-one ever seems to bring this potential problem to the attention of customers.That seems mad to me.
Ok.I'm trying to reconcile different responses here. Your curt answers are at odds with the more helpful responses here.
That didn't work, did it?One person is saying contact the DNO.
He didn't actually say that.Another is saying that the required resistance may not even be achievable except with a short cable
But they aren't and don't have to be, so...- meaning kitchens with hobs have to be very near the CU.
I only said no when it was the answer to your questions.You're just saying "no". Super helpful, thanks.
I have to say, in the strongest possible terms, that I strongly disagree with you. I have been called to countless TN-S and TN-C-S supplies where the Ze has been outside the spec, often wildly.It seems fairly unlikely that the DNO-supplied earth is significantly 'high resistance'. A TN-S earth is allowed to have a Ze of up to 0.8Ω - so, unless the cooker circuit is pretty short in length, the measured Ze of 1.19Ω would seem to be quite credible(if the Ze of the DNO earth was close to the 'maximum allowed).
So I fear I might pay someone £120 p/h, not agreeing to a fixed price/time, and then them telling me either they can't do the tests required (as @ericmark says), or that they do do the tests and it's a high Ze but still under 0.8Ω (as @JohnW2 said). And then I've spent hundreds and still no closer to just replacing a hob. :sigh:How? Only way I know what size fuse I have is I was there when new meter fitted. They have seals on them. I have in the past used the enquiry methods to get the Ze, the DNO should have it on record, if not they have to send some one out to measure.
We may be on a ring, (not ring final) and that ring allows sections to be isolated while retaining the supply for work to be carried out, so the Ze can vary depending on if the ring is split or not when the measurement is made. So in theroy the domestic electrician can't work out normal Ze as he has no idea of how supplied when he measures.
So that makes no sense.
I'm not incompetent!Some of your responses have been from retired sparks or diyers
You need a local competent spark - then and only then will you know what to do next