Cables are designed to run at upto 70 degrees. This is normal.
I'm going to request this thread is locked to save a lot of people existing their time for you.
I'm sorry but a cable running at 70 degrees is not normal. It may be rated to run up to 70degrees but a cable that is warm to the touch is a clear sign of something being wrong. At 27amps on a 2.5mm cable the heat produced per foot of cable length is around 1.5watts equiv. At 16 amps (32amp ring final) it's less than half a watt. In order for the cable to heat up to a point where it is warm to the touch you would need around 45amps pumping through a 2.5mm cable. If the cable is wrapped in high performance insulation that figure might be more like 35 amps. Either way, stupid numbers.
Further leaching of PVC occurs due to heat, not due to the compounds in hot glue. Hot glue melts around 100-120 degrees and stays at that temperature for less than 30 seconds. Time is the second factor associated with leaching. If the cable is rated to 70 degrees then the leaching that may or may not occur would occur regardless of the presence of hot glue.
Your comments illustrate why I don't simply take every little bit of dumbarse advice. You are clearly less competent than I am.
This thread is serving as both a blog and a place for me to ask questions. If you don't want to participate that's your prerogative.