yesterday we had an electrician in to wire the new shower, as part of that the RCD was replaced (only rated at 60A before), tested out ok and everything, when the job was done, the new circuit fully tested and everything, the mcbs for the rest of the board were switched back on, the kitchen ring which was the last one to be flicked on took out the RCD, unplugging the microwave solved it, thought maybe the old rcd was kaput and the microwave was faulty.
Anyway, kept getting nuisense trips, and when I investigated the microwave found out that it wasn't faulty as such but the filter board was leaking 2.2ma to earth (multimeter* in series with the functional earth), and microwave plugged in, the last circuit to be switched on tripped it, obviously we have combined leakage nearly tripping it, and the microwave pushing it over the edge. Temporary measure has to been to use the 'backup' microwave, but I want to find out where the rest of the leakage is comming from (because with it that close to the mark we still get nuisence trips without the big microwave), I was planning on getting hold of a clamp meter and putting it round both tails and switching on each circuit indiviudally, then dropping down to testing appliances by plugging them in one at a time. I'm hopeing though to find it to be something daft like moist dust in an outdoor junction box or something.
Just wondered if anyone else had any ideas to throw into the mix
*A new one, accepted that my old one had died
Anyway, kept getting nuisense trips, and when I investigated the microwave found out that it wasn't faulty as such but the filter board was leaking 2.2ma to earth (multimeter* in series with the functional earth), and microwave plugged in, the last circuit to be switched on tripped it, obviously we have combined leakage nearly tripping it, and the microwave pushing it over the edge. Temporary measure has to been to use the 'backup' microwave, but I want to find out where the rest of the leakage is comming from (because with it that close to the mark we still get nuisence trips without the big microwave), I was planning on getting hold of a clamp meter and putting it round both tails and switching on each circuit indiviudally, then dropping down to testing appliances by plugging them in one at a time. I'm hopeing though to find it to be something daft like moist dust in an outdoor junction box or something.
Just wondered if anyone else had any ideas to throw into the mix
*A new one, accepted that my old one had died