Well - after my last set of adjustments, it's been running for a week, no lock outs, no WOOF when it starts, no smoke, no smells, and it's been on the timer for the second time, so on at 05:00, off at 10:00, on at 15:00 and off at 23:30. First time I tried this, it locked out when trying to restart on the afternoon or morning shift, not any more. There is NO smoke, at all, nothing. The pump was checked at 8.8 bar - Riello state for our setup it needs to be 9 bar, and the air damper set to 6.5 as per Riello again. CO2 at 10.8.
When is the Grand National
I'm very pleased with it all now, but still seem to wake at 05:00 and hear it fire up....just checking...the next job will be to install a non return valve at the bottom of the pipe just before it turns to go up the wall, and another at the top to stop it running back down again, as this should take some of the strain off the Danfoss pump (sounds a bit rattly sometimes) and keep the fuel line charged all the time.
Thanks for all your input and info.
Andrew.
When is the Grand National
I'm very pleased with it all now, but still seem to wake at 05:00 and hear it fire up....just checking...the next job will be to install a non return valve at the bottom of the pipe just before it turns to go up the wall, and another at the top to stop it running back down again, as this should take some of the strain off the Danfoss pump (sounds a bit rattly sometimes) and keep the fuel line charged all the time.