Tripping rcd

I think the frequancy may be a red herring, ...
Indeed. In fact, if there were a theoretical need for a Type F RCD (which I somewhat doubt), then I thought that the potential problem with not having one would be that the RCD might not trip when it should, rather than it tripping when it shouldn't?
one looks at other things first, the insulation tester and clamp on ammeter are the first tools. ... However he says an electrician has been employed, so one assumes run of mill tests already done, so assuming no fault found, one then has to look at more unusual causes.
All probably true.

Kind Regards, John
 
Sponsored Links
Thanks for all your input guys, the fault turned out to be the lmmersion/element, even though it wasn’t being used, suspected earth leakage going through the neutral, during fault finding if he disconnected the earth on the immersion the fault still happened but when he disconnected the neutral and earth the fault disappeared, put new immersion in and all good.
As I said I’m not a sparky so don’t understand why and how but that was the solution, thanks
 
This is why an RCD will trip on an Neutral to Earth fault when the faulty circuit is not switched on but something else is taking current.

rcd trip 2022.jpg
 
Sponsored Links
Would the above do it without load?? The immersion wasn’t being used and also isolated by a circuit breaker inside the appliance??
 