Tripping ring main

And any FCU has been switched off, not just fuse removed.

Assuming the fuse is in the live - then it out to be enough. From what the OP has posted, it suggests a L to E fault, enough to trip the RCD, not enough to trip the MCB.

So yes question why 20 minutes before tripping, what has a 20 minutes delay?

Which was why I suggested water, or moisture - it will gradually become more conductive, as time passes..
 